Questions about GFM renewable energy system establishing. #431

Answered by jinningwang
xiaoheimai95 asked this question in Q&A
Discussion options

You must be logged in to vote

Hello @xiaoheimai95,

Thanks for your interest.
As far as I know, there are no existing separate control modules for REGCV1, REGCV2, REGF1, REGF2, and REGF3. For now, you can directly control the modules themself. New control algorithms might require additional development.

Failed initialization involves failed power flow and failed TDS initialization. Failed power flow is usually caused by a large gap in power balance. For this, you can check the power flow devices. Some additional discussions are available in pandapower interface discussion for more information. As for failed TDS initialization, the following discussions might be helpful: Question about Initialization, EI System Initiali…