Time series load flow calculation #283

Answered by SanPen
fapermata8 asked this question in Q&A
Discussion options

You must be logged in to vote

Hi!

I believe the discrepancy is due to fact that the reactive power in generation devices is calculated if the device is_controlled property is true.

This is, gerators make buses PV and in PV buses, Q is calculated regardless of what Q or pf you specify...if is_controlled = true, else the bus is PQ and the reactiva power estimate remains.

Then, where does Q come from at the inputs analysis? An initial Q estimate is generated with the generator power factor (pf) but that estimate is corrected by the power flow algorithm if is_controlled = true.

I hope this helps