Mass-flow rate distribution in meshed network #494
-
Hello everyone! I'm trying to simulate a small and simple district heating network with one source and two loads (as heat exchangers) following a tutorial. Figure of the network and model is here:
I set a mass-flow for a source pump of 20 kg, and temperature difference of 45 deg C. That will give an input power around 4.167x20000x45 = 3 750 300 W or 3750 kW. Next, I set two exchanger stations with 1500 kW of load each. I would assume that the same loads would get more or less equal mass flow distributions between them (around 10 kg/s each). However, the result I get, that almost all the mass flow (19.999 kg/s) goes to the fisrt heat echanger (HE1), and only 0.0001 kg/s goes to pipe PS2 and to HE2. Due to this the temperature difference in HE2 becomes inadequate. Is there any parameters that affect this mass flow rates distribution? |
Beta Was this translation helpful? Give feedback.
Replies: 3 comments 7 replies
-
Hi @MikhailSkl, maybe the pressure drop at P2S and P2R is too high, so that the flow rate becomes very low. The problem should become smaller, if the diameters for these pipes are increased. Apart from that, a flow control component has been added to pandapipes as of Version 0.8. With this component, a mass flow set point between two junctions can be defined. It could be well suited for your situation. |
Beta Was this translation helpful? Give feedback.
-
Dear @MikhailSkl ,
The suggestion to just increase the pipe diameters will probably not help much, as this does not change the fact that the resistance in HE1 remains 0. |
Beta Was this translation helpful? Give feedback.
-
I think I have to make an update here. The new controlling component is already included in the latest release, it's called flow_control and can be created like any other component. |
Beta Was this translation helpful? Give feedback.
Dear @MikhailSkl ,
in general, @jkisse is right, but I would like to shift the focus a little: The resistance rates of the two paths through the heat exchangers are extreme. Actually it would make sense if the flow through P2S and P2R would be 0, because there is a resistance of this pipe while there is no resistance in the heat exchanger HE1. So, if there is no pressure drop between J2S and J2R, any flow through P2S and P2R will create a higher pressure drop than that. So, I am not sure what exactly you would like to simulate, but here are some suggestions: